Flexible Connectors.

Posted: May 4th, 2017, 5:54 pm
by SimonG
A lot of people have had flexible connectors burst or leak. Some may even think of them as the devils work.
But I find them useful and a lot of taps now come with flexies rather than hard piped.

The important things to remember are.

Don't kink the connector when installing. It will create a weak point and disrupt the flow to the tap.

Don't allow the connector to twist. It will stress it and potentially lead to failure.

Don't fasten them directly onto isolating valves. The rubber on the connector can be cut on the chamfer of the isolation valve. Fasten a spare radiator tail into the isolation valve first. This gives a flat surface for the connector to seal too.

Re: Flexible Connectors.

Posted: May 4th, 2017, 6:42 pm
by RPM
However there are now isolation valves with a flat surface being sold.

Re: Flexible Connectors.

Posted: May 7th, 2017, 12:19 pm
by Mr KJ
Justpumps+ wrote:However there are now isolation valves with a flat surface being sold.
Probably not cost effective though.
I have a pile of rad tails which work well

Sent from my SM-G920F using Tapatalk


Re: Flexible Connectors.

Posted: May 7th, 2017, 12:21 pm
by Mr KJ
Thus is why you should regularly inspect the codition of your hoses if you have them in your house.Image

Sent from my SM-G920F using Tapatalk


Re: Flexible Connectors.

Posted: May 7th, 2017, 12:41 pm
by RPM
Mr KJ wrote:
May 7th, 2017, 12:19 pm
Justpumps+ wrote:However there are now isolation valves with a flat surface being sold.
Probably not cost effective though.
I have a pile of rad tails which work well

Sent from my SM-G920F using Tapatalk
Heard about the rad tails, Williams sell the isolation valves if you use them.

Re: Flexible Connectors.

Posted: May 7th, 2017, 12:53 pm
by Mr KJ
Once upon a time these just got thrown in the scrap pile.
But now i save them

Toolstation sell a similar thing for connecting hoses which are probably cheaper than flat faced iso's if you run out of tailsImage

Sent from my SM-G920F using Tapatalk


Re: Flexible Connectors.

Posted: May 7th, 2017, 12:58 pm
by Mr KJ
Hers the toolstation product.
Note they do them in 3/8" as well.
Image

Sent from my SM-G920F using Tapatalk


Re: Flexible Connectors.

Posted: May 7th, 2017, 7:26 pm
by JC Plumb
Called out to this last week. No signs of kinks, was installed perfectly. My guess is the installer twisted it while tightening it up.
Image
Image

Re: Flexible Connectors.

Posted: May 7th, 2017, 8:10 pm
by jonnyswamp
I recently changed a split flexi in a dentist surgery in Cardiff
It burst on a Friday evening (upstairs patients w/c) and run full bore until it set the fire alarms off in the morning (caused a short probly)
Don't know the final figure, but it includes most ceilings, downstairs floor coverings and 2 dentist chairs at around £30,000 each
So if they are used, follow SimonG's advice and also check them now and again as you will sometimes see signs of bulges or fraying braid before they burst

Re: Flexible Connectors.

Posted: May 8th, 2017, 10:58 am
by MrTom
Like most things there are cheap naff ones and more expensive decent ones. I have seen, used and fitted both and unfortunately they look and feel very similar. I haven't seen many issues other than them being overtightened into a monobloc tap

Re: Flexible Connectors.

Posted: September 29th, 2017, 10:37 pm
by YorkshireDave
Does anyone one else have a problem with the advertised bore of these?

If advertised as a 13mm bore what would you expect the bore of the hose to be?

Re: Flexible Connectors.

Posted: September 30th, 2017, 8:34 pm
by REDSAW
YorkshireDave wrote:
September 29th, 2017, 10:37 pm
Does anyone one else have a problem with the advertised bore of these?

If advertised as a 13mm bore what would you expect the bore of the hose to be?
half inch?

Re: Flexible Connectors.

Posted: September 30th, 2017, 9:08 pm
by YorkshireDave
just over if we're being pedantic ;)

So, would it be unreasonable to expect it to be 13mm all the way through?

Re: Flexible Connectors.

Posted: October 1st, 2017, 10:24 am
by joni os
The cross section area is the important criteria. A circle will always give a greater cross section area than an oval of equal perimeter. Bends create non circular cross sections. Flexis are used where bends are necessary hence the problem. In many cases I find a length of Hep2O with push fit couplers will perform better than a braided flexi. has the advantage of being cut to the correct length, rotates freely at connections and being readily available (length of pipe and connectors in van) works out cheaper. Where possible a properly bent copper pipe will always be the superior solution.

Re: Flexible Connectors.

Posted: October 1st, 2017, 11:09 am
by YorkshireDave
Quite agree. Perhaps however I should come clean. Fact is if you have a 100mm dia pipe that drops down to 10mm then goes back up to 100 its bore is 10mm due to the limitation to flow.

All of these flexies mention a bore that relates to the rubber hose ONLY. When you measure the minimum dia of the fittings at the ends they drop to closer to 6mm. So, we are being lied to at best and ripped off at worse. :x :x :x

Re: Flexible Connectors.

Posted: October 1st, 2017, 12:12 pm
by joni os
Following above logic a 12 bore shotgun with full choke would not be a 12 bore. Even worse the," less aware," could claim a gas boiler with 15mm gas connection only needs 15mm pipework from meter.

Re: Flexible Connectors.

Posted: October 1st, 2017, 1:40 pm
by Best
Same with modern bath taps on gravity supply, - old taps had 3/4" works and full flow, but the new taps with 1/2" works just don't flow the same. We are being ripped off with inferior products.
As to flexis - I had to replace a burst flexi on mains last week that was connected to a monobloc 15mm pipe. It appeared ok and not twisted and not bent much. I just machine bent a 90 degree piece of copper pipe and used a 15mm compression elbow and it took just 5 minutes to install. I can't see the reason to use flexis where a copper pipe, or plastic pipe would do better job.

Re: Flexible Connectors.

Posted: October 1st, 2017, 4:41 pm
by REDSAW
AH!, yes on the tap connectors it goes down to about 6mm.
the straight connectors bores are all through sized.
i like the idea of using plastic on toilet connections instead so i may try that next time on a twisty fit.

i believe also those hoses split after the stainless braid wire is twisted-brakes a strand then perforates the rubber lining causing a pressure rupture.

Re: Flexible Connectors.

Posted: October 1st, 2017, 11:13 pm
by YorkshireDave
joni os wrote:
October 1st, 2017, 12:12 pm
Following above logic a 12 bore shotgun with full choke would not be a 12 bore. Even worse the," less aware," could claim a gas boiler with 15mm gas connection only needs 15mm pipework from meter.
Joni. Get your point but disagree with the outcome.

Fact is, YOU as the owner choose to choke your 12 bore. When YOU remove whichever choke you are using the gun goes back to being a 12 bore or 10 if you're a bit younger.

These flexis are advertised as being 13mm and they charge more for the larger bore. And yet, the real, unchangable bore is, as I've already said, closer to 6/7mm which patently limits flow permanently vs a 13mm bore. Oh, as if you didn't know, we are talking a completely different issue with gas so that's a red herring. Just chuck it back in the sea where it belongs...

We are being charged for something almost none of these flexible hoses deliver. Personally I do not feel that is right and proper as I don't want to rip my customers off and neither do I wish to be ripped off. If you are happy with that that's between you and your customers/bank manager ;)

Re: Flexible Connectors.

Posted: October 1st, 2017, 11:26 pm
by YorkshireDave
Best wrote:
October 1st, 2017, 1:40 pm
Same with modern bath taps on gravity supply, - old taps had 3/4" works and full flow, but the new taps with 1/2" works just don't flow the same. We are being ripped off with inferior products.
As to flexis - I had to replace a burst flexi on mains last week that was connected to a monobloc 15mm pipe. It appeared ok and not twisted and not bent much. I just machine bent a 90 degree piece of copper pipe and used a 15mm compression elbow and it took just 5 minutes to install. I can't see the reason to use flexis where a copper pipe, or plastic pipe would do better job.
Dont get me started... Once again this is corporate avaris taking advantage of the fact that there's no formal definition of low or high pressure for a domestic water environment. There is a 'level' of consensus that open vented systems are 'low pressure' but there is no legal definition, no upper and/or lower limits. It's for this reason a tap manufacturer can say 0.5 bar is low pressure. Some poor homeowner puts a 0.5 bar tap in a bathroom with the CWS just above on the joists and they find they can pee faster but they have no comeback...

Some 'after market' cartridge manufacturers, can think of one not yet on the market, have specifically designed their cartridges to truly maximise flow through them. That said, the fundamental design was driven by a Yank where, of course, hot water systems are high pressure. They never designed them to take over in low pressure circumstances. It was lower cost to manufacturer and inbuilt obsolescence that drove their use to today's levels. Sorry! History lesson over.

Tap manufacturers buy on two principal criteria - looks and price. With the exception of some Pegler taps, the rest don't give a flying fig about performance. Their view is 'state the minimum operating pressure (NOT optimum) and let the mugs (sorry buyers) beware'.

Re: Flexible Connectors.

Posted: October 1st, 2017, 11:34 pm
by YorkshireDave
REDSAW wrote:
October 1st, 2017, 4:41 pm
AH!, yes on the tap connectors it goes down to about 6mm.
the straight connectors bores are all through sized.
i like the idea of using plastic on toilet connections instead so i may try that next time on a twisty fit.

i believe also those hoses split after the stainless braid wire is twisted-brakes a strand then perforates the rubber lining causing a pressure rupture.
Lastly... We have done some research. Strangely we initially thought it would be the braid piercing too. It turns out to be much simpler - when they installed correctly. It's poor quality pipe, basically with walls with air pockets as its cheap. The continual cycling (raising and lowering) of pressure causes the pipes to fail at these weak spots created when the rubber pipes is made.

Many people think a WRAS approved pipe is better quality.THEY ARE NOT. They are the same cheap rubber but its been tested to not contaminate the potable water it's in contact with. WRAS does NOT denote quality of manufacture or performance. They are still made cheaply in their squillions. They are much more expensive to buy because the WRAS approval process costs two arms and a leg and they have to recoup those costs.

Re: Flexible Connectors.

Posted: October 2nd, 2017, 8:55 am
by joni os
The only red herrings here, are people getting incensed about reduction of flow through end connections, when they will happily put a reduced bore iso valve on the same pipework. Plumbing is a Trade not a DIY weekend pastime and any of us fitting a 0.5bar tap would caution if CWS was less than 5 metres above outlet. With water, like gas, pressure drop per unit length is a consideration. Hence 120 metres of MDPE mains supply pipe is recommended to be 50mm bore even though the water meter is 3/4". Esoteric terms are common to all Trades, uses and limitations understood and applied accordingly.

Re: Flexible Connectors.

Posted: October 2nd, 2017, 10:11 am
by YorkshireDave
"People"... At least have the courage to say what you mean.

I consider myself my customers champion so take what is installed on their behalf seriously - every bit of it. If that upsets you I apologise but I'll never stop because it's my job to protect them as well as install.

Have a nice day.

Re: Flexible Connectors.

Posted: October 2nd, 2017, 10:27 am
by joni os
Keep posting Dave, your contributions liven the forum. But as for being the customer's champion: Weren't you suggesting, regarding quarter turn taps, we should replace £2.50 of parts and charge for new valve. I heard richard Turpin rode to York but never realised he still lived there.

Re: Flexible Connectors.

Posted: October 2nd, 2017, 11:15 am
by YorkshireDave
touche... ;-)

That said, and in my defence, you ARE still delivering a brand new performing tap at many times less than manufacturers prices or the cost of a new tap.

Re: Flexible Connectors.

Posted: October 2nd, 2017, 5:02 pm
by REDSAW
and ceramic tap valves are lesser output size when fully opened than the iso or tap connectors bore- more pressure less flow :?

Re: Flexible Connectors.

Posted: October 2nd, 2017, 8:07 pm
by YorkshireDave
Truth is they vary considerable - hugely in fact.
Many just manage a cross sectional area equiv of 6mm dia but the good ones do closer to 9mm Whilst that doesn't sound much difference its actually 19 sq mm versus 28 sq mm. A traditional (multi-turn valve inlet (12mm) is 38 sq mm. So, common cartridge = 50% of flow at best, good cartridge = >73%
On a low pressure system (by that I mean up to 0.2 bar) that makes a massive difference to flow rates and usability

Re: Flexible Connectors.

Posted: October 2nd, 2017, 10:12 pm
by joni os
Cross section area 6mm dia. is 28.278 sq mm. For 9mm dia its 63.626 sq mm. Don't dispute the overall conclusion but it would be more convincing if the maths was correct.

Re: Flexible Connectors.

Posted: October 2nd, 2017, 10:33 pm
by YorkshireDave
That's what you get for being old and trying to remember instead of checking carefully as you did.
Thank you for the correction.

Re: Flexible Connectors.

Posted: October 2nd, 2017, 11:23 pm
by joni os
No problem Dave. As a general rule when calculating cross section of circle I treat diameter as side of square and deduct 20% from answer. Eg 9 X 9 = 81 less 20% (16.2) equals 64.8 The true answer is slightly less, as above. Useful when checking ventilation etc. only requires calculator in border line cases. This is why your figures shouted error. Don't be hard on your memory, I suspect it was remembering relative perimeters.